AIO Standard V4.5 – IP Address 120 When Cold and Steer Not Working
AIO Standard V4.5 – IP Address 120/121 When Cold and Steer Not Working
An AgOpenGPS AIO Standard V4.5 board with a Teensy 4.1 showed a temperature-dependent fault. At room temperature, the Steer module correctly appeared at IP address 192.168.5.126. However, after cooling the board below approximately 10 °C, the address changed to 192.168.5.120 or 192.168.5.121, and Steer remained red.
Cause of the Problem
Diagnostic firmware showed that the integrated ADS1115 converter changed its I²C address when cold:
  • correct address 0x48 → IP .126,
  • incorrect address 0x49 → IP .121,
  • no response from the ADS1115 → IP .120.
The cause was an unconnected, “floating” ADDR input on the integrated ADS1115. At room temperature, it happened to be interpreted as GND, so the ADS1115 used the correct address 0x48. When cold, however, it could be interpreted as VDD, changing the address to 0x49.
Solution
The ADDR input – pin 1 of the ADS1115 was permanently connected with a thin wire to the GND pin on the header intended for an external ADS1115 module, as shown in the attached photograph. After this modification, the ADS1115 consistently uses address 0x48, and the board receives IP address 192.168.5.126 even when cold.
After this hardware modification, the original standard firmware can be used. The problem was not caused by the network or AgOpenGPS settings, but by the unstable I²C address of the integrated ADS1115.
Let me know if anyone has ever had a similar problem.
Well done for working out the issue and fixing it.
Ive personally never heard of this issue before
I’m using the same AIO v4.5 Standard board. It happens randomly. Sometimes it’s when I engage autosteer by CANBUS, and other times it’s when the steering angle changes quickly. The WAS reading suddenly jumps to −50° and stays there even when I turn the wheels. The only way I’ve found to get it working again is to power-cycle the whole AIO board.
Did you see anything like that before you grounded pin 1 on the ADS1115?
No, I haven’t encountered this; it has never happened that the WAS value alone got stuck once the steering system had already connected (indicated by the color green). In my experience, either the steering system wouldn’t connect at all (remaining red), or—if it did connect (turning green)—the WAS worked without any issues. The fault you are describing appears to be different.